Select Page

Fans in recovery room

Home Forums Infexion Connexion Fans in recovery room

 | Click to Receive Email Notifications of Posts
Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #73518
    Anonymous
    Inactive

    Author:
    Anonymous

    Organisation:

    State:

    Hi everyone,

    A facility has recently purchased a large wall mounted oscillating fan and
    installed it in the area where the porters remake beds / trolleys and this
    area is open to the recovery room.

    I am concerned about disruption of the air flows and the potential risks
    associated with blowing particulates [from linen used to make up the
    trolleys] around the facility.

    However I have been challenged to provide evidence that fans pose a risk of
    infection and / or evidence that fans should not be used in this
    environment.

    A quick google search and review of ACORN Standards reveals little – so I am
    hoping someone else may have come across this issue and can provide some
    assistance.

    All feedback gratefully received.

    Kind Regards

    Terry McAuley

    Sterilisation & Infection Prevention and Control Consultant

    STEAM Consulting Pty Ltd ACN 604 439 698

    E: terry@steamconsulting.com.au

    W: http://www.steamconsulting.com.au

    A: PO BOX 779

    Endeavour Hills

    VIC Australia 3802

    CONFIDENTIAL COMMUNICATION: The information contained in this message may
    contain confidential information intended only for the use of the individual
    or entity named above. If the reader of this message is not the intended
    recipient, you are hereby notified that any dissemination, distribution or
    duplication of this transmission is strictly prohibited. If you have
    received this communication in error, please notify us by telephone or email
    immediately and return the original message to us or destroy all printed and
    electronic copies. Nothing in this transmission constitutes an agreement of
    any kind unless otherwise expressly indicated.

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to aicalist@aicalist.org.au

    To send a message to the list administrator send an email to aicalist-request@aicalist.org.au.

    You can unsubscribe from this list be sending ‘signoff aicalist’ (without the quotes) to listserv@aicalist.org.au

    #73519
    Michelle Bibby
    Participant

    Author:
    Michelle Bibby

    Email:
    michelle@INFECTIONPREVENTION.COM.AU

    Organisation:
    Infection Prevention Australia

    State:

    HI Terry

    It is unfortunate that common sense does not prevail and also unfortunate
    that a reference is required to support what would appear to be such a
    simple issue to resolve.

    I would support 100% that a fan in this area is not acceptable and will see
    if I can find something as I am sure there is somewhere

    Thanks
    Michelle

    Michelle Bibby
    Infection Prevention Australia
    +61 429 071 165
    Michelle@infectionprevention.com.au
    http://www.infectionprevention.com.au

    Terry McCauly

    Hi everyone,
    A facility has recently purchased a large wall mounted oscillating fan and
    installed it in the area where the porters remake beds / trolleys and this
    area is open to the recovery room.
    I am concerned about disruption of the air flows and the potential risks
    associated with blowing particulates [from linen used to make up the
    trolleys] around the facility.
    However I have been challenged to provide evidence that fans pose a risk of
    infection and / or evidence that fans should not be used in this
    environment.
    A quick google search and review of ACORN Standards reveals little so I am
    hoping someone else may have come across this issue and can provide some
    assistance.
    All feedback gratefully received.
    Kind Regards
    Terry McAuley
    Sterilisation & Infection Prevention and Control Consultant
    STEAM Consulting Pty Ltd ACN 604 439 698
    E: terry@steamconsulting.com.au
    W: http://www.steamconsulting.com.au
    A: PO BOX 779
    Endeavour Hills
    VIC Australia 3802

    CONFIDENTIAL COMMUNICATION: The information contained in this message may
    contain confidential information intended only for the use of the individual
    or entity named above. If the reader of this message is not the intended
    recipient, you are hereby notified that any dissemination, distribution or
    duplication of this transmission is strictly prohibited. If you have
    received this communication in error, please notify us by telephone or email
    immediately and return the original message to us or destroy all printed and
    electronic copies. Nothing in this transmission constitutes an agreement of
    any kind unless otherwise expressly indicated.
    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO
    NOT REPRESENT THE OPINION OF ACIPC.
    The use of trade/product/commercial brand names through the list is
    discouraged by ACIPC. If you wish to discuss specific reference to products
    or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives
    registration and login required.

    Replies to this message will be directed back to the list. To create a new
    message send an email to aicalist@aicalist.org.au

    To send a message to the list administrator send an email to
    aicalist-request@aicalist.org.au.

    You can unsubscribe from this list be sending ‘signoff aicalist’ (without
    the quotes) to listserv@aicalist.org.au

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to aicalist@aicalist.org.au

    To send a message to the list administrator send an email to aicalist-request@aicalist.org.au.

    You can unsubscribe from this list be sending ‘signoff aicalist’ (without the quotes) to listserv@aicalist.org.au

    #73520
    Glenys Harrington
    Participant

    Author:
    Glenys Harrington

    Email:
    infexion@ozemail.com.au

    Organisation:
    Infection Control Consultancy (ICC)

    State:

    Hi Terry,

    I would ask the hospital to provide an engineer assessment to confirm the
    room air was not entrained into the clean airstream of the operating
    theatre.

    I’d also focus on the dispersion of lint and fibre on air currents in the OR
    complex – plenty of evidence for low lint OR environments.

    In addition I would point out to the organisation that fans may also be a
    red flag to surveyors that a temperature control or ventilation problem
    exists, which can impact equipment and overall patient care.

    Find below and attached some information that may be of interest/use.

    Some information form the Joint Commission (USA) web page – Standards FAQ
    Details

    Fans – patient Care areas

    Are fans allowed in patient care areas, laboratories, or other support areas
    in an organisation?

    There are no specific Joint Commission standards that prohibit the use of
    fans. While fans may be used for additional comfort of the patient, such as
    those with respiratory distress or post cardiac surgery, they may indicate
    to surveyors that a temperature control or ventilation problem exists, as
    described by EC.02.06.01. Space temperature issues can impact equipment,
    patient testing results, and overall patient care. This concern usually
    arises after adding equipment or use of the space without increasing the
    capability of space cooling/ventilation. The organization should perform a
    risk assessment, per EC.02.01.01 that includes the most appropriate persons
    available to the organization. Examples of assessment concerns could
    include: risks pertinent to the needs of the patient; ventilation and/or
    temperature concerns for equipment; airborne particles/contamination that
    may impact patient care, procedure/treatment processes or equipment
    operation; maintaining the cleanliness of fan blades/housing; possible
    tripping hazard(s) created by cords; etc. Infection control should be a key
    element in the assessment process. The survey process will evaluate the risk
    assessment for effectiveness and validate proper implementation of the
    resulting policy/practice. Adjustments to the implemented process are to be
    made as needed. [EC.02.06.01]

    https://www.jointcommission.org/standards_information/jcfaqdetails.aspx?Stan
    dardsFaqId76
    &ProgramId

    INFECTION PREVENTION & CONTROL COMMUNICATION FORM PORTABLE FANS – CLEANING
    AND USE RESTRICTIONS – Winnipeg Regional Health Authority, Acute Care
    Infection Prevention & Control Manual – DATE ISSUED: October 22, 2015

    “Portable fans are currently used in some sites across the region to assist
    in patient comfort or to regulate a patient’s body temperature. Other sites
    have chosen to disallow the use of fans in patient care areas. Staff also
    use fans in their work areas, which may be near patients. This communication
    form does not supersede any existing site specific policy which bans the use
    of fans, nor does it include High-Efficiency Portable Air (HEPA)-filtered
    fans. Fans have the potential to disperse dust and airborne-transmitted
    microorganisms1 , create airborne Clostridium difficile spores3 , and alter
    airflow patterns. While use of portable fans has not been proven to transmit
    infection3 , these issues, as well as lack of appropriate cleaning
    procedures, are infection control concerns”.

    DO FANS SPREAD INFECTION IN CLINICAL AREAS? Emerg Med J 2008;25:10 689

    http://emj.bmj.com/content/25/10/689.1.extract

    https://www.ncbi.nlm.nih.gov/pubmed/18843075

    regards

    Glenys

    Glenys Harrington

    Infection Control Consultancy (ICC)

    P.O. Box 6385

    Melbourne

    Australia, 3004

    M: +61 404816434

    E: infexion@ozemail.com.au

    Of Terry McAuley

    Hi everyone,

    A facility has recently purchased a large wall mounted oscillating fan and
    installed it in the area where the porters remake beds / trolleys and this
    area is open to the recovery room.

    I am concerned about disruption of the air flows and the potential risks
    associated with blowing particulates [from linen used to make up the
    trolleys] around the facility.

    However I have been challenged to provide evidence that fans pose a risk of
    infection and / or evidence that fans should not be used in this
    environment.

    A quick google search and review of ACORN Standards reveals little – so I am
    hoping someone else may have come across this issue and can provide some
    assistance.

    All feedback gratefully received.

    Kind Regards

    Terry McAuley

    Sterilisation & Infection Prevention and Control Consultant

    STEAM Consulting Pty Ltd ACN 604 439 698

    E: terry@steamconsulting.com.au

    W: http://www.steamconsulting.com.au

    A: PO BOX 779

    Endeavour Hills

    VIC Australia 3802

    CONFIDENTIAL COMMUNICATION: The information contained in this message may
    contain confidential information intended only for the use of the individual
    or entity named above. If the reader of this message is not the intended
    recipient, you are hereby notified that any dissemination, distribution or
    duplication of this transmission is strictly prohibited. If you have
    received this communication in error, please notify us by telephone or email
    immediately and return the original message to us or destroy all printed and
    electronic copies. Nothing in this transmission constitutes an agreement of
    any kind unless otherwise expressly indicated.

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO
    NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is
    discouraged by ACIPC. If you wish to discuss specific reference to products
    or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives
    registration and login required.

    Replies to this message will be directed back to the list. To create a new
    message send an email to aicalist@aicalist.org.au

    To send a message to the list administrator send an email to
    aicalist-request@aicalist.org.au.

    You can unsubscribe from this list be sending ‘signoff aicalist’ (without
    the quotes) to listserv@aicalist.org.au

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to aicalist@aicalist.org.au

    To send a message to the list administrator send an email to aicalist-request@aicalist.org.au.

    You can unsubscribe from this list be sending ‘signoff aicalist’ (without the quotes) to listserv@aicalist.org.au

Viewing 3 posts - 1 through 3 (of 3 total)
  • The forum ‘Infexion Connexion’ is closed to new topics and replies.