Select Page

Exhaust Vents above Sterilisers in Sterilising Services Departments.

Home Forums Infexion Connexion Exhaust Vents above Sterilisers in Sterilising Services Departments.

 | Click to Receive Email Notifications of Posts
Viewing 5 posts - 1 through 5 (of 5 total)
  • Author
    Posts
  • #77307
    Anonymous
    Inactive

    Author:
    Anonymous

    Organisation:

    State:

    Good Morning One and All

    During a recent audit we had a recommendation regarding the placement of outlet vents in the ceiling above the Steriliser doors.
    Temperatures in our CSSD Department become quite warm so looking for a reference that supports this
    Can anyone assist please

    Most appreciated.
    Liz Vanderlinde
    Infection Prevention Control Co-ordinator
    North West Private Hospital
    [Description: hca_luye_logo]
    Brickport Road, Burnie TAS 7320, Australia
    T +61 3 6432 6005 F +61 3 6431 5766
    E liz.vanderlinde@healthecare.com.au W healthecare.com.au
    Healthe Care Hospitals are accredited by ACHS NSQHS Standards or ACHS EQuIP National
    [Description: achs][Description: equip]
    QIC Standards
    [Description: qic]

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to acipclist@acipc.org.au

    To send a message to the list administrator send an email to admin@acipc.org.au

    You can unsubscribe manually from this list by sending ‘signoff acipclist’ (without the quotes) to listserv@aicalist.org.au

    #77309
    Brett
    Participant

    Author:
    Brett

    Email:
    brett@BIOSAFETY.COM.AU

    Organisation:

    State:

    Hi Liz

    Thanks for the email. There are several Australian Standards that relate to this topic and ventilation requirements. I would refer you to the following which are both Steam Sterilzer specific and General:

    Australian standards

    https://www.standards.org.au/standards-catalogue/sa-snz/health/me-003

    Also AS/NZS 2243.3 is a great Reference.

    https://infostore.saiglobal.com/en-us/standards/as-nzs-2243-3-2010-117305_saig_as_as_273922/

    I hope that this assists.

    Kindest regards
    Brett Cole,
    B. Sc (Hons) M. Occ. Hyg. & Tox. CBP (IFBA) MABSANZ
    Occupational Hygienist – Biological Control Unit/Managing Director
    [cid:image001.jpg@01D68B50.4CCB8860]
    Unit 15, 69 Acacia Road, Ferntree Gully Victoria Australia 3156
    Please visit our website http://www.biosafety.com.au
    _______________________________________________________________________
    This message contains confidential information and is intended only for the individual named. If you are not the named addressee you should not disseminate, distribute or copy this e-mail. Please notify the sender immediately by e-mail if you have received this e-mail by mistake and delete this e-mail from your system. E-mail transmission cannot be guaranteed to be secure or error-free as information could be intercepted, corrupted, lost, destroyed, arrive late or incomplete, or contain viruses. The sender therefore does not accept liability for any errors or omissions in the contents of this message, which arise as a result of e-mail transmission. If verification is required, please call 1800 379 996 or PO BOX 101 Ferntree Gully Vic 3156

    Good Morning One and All

    During a recent audit we had a recommendation regarding the placement of outlet vents in the ceiling above the Steriliser doors.
    Temperatures in our CSSD Department become quite warm so looking for a reference that supports this
    Can anyone assist please

    Most appreciated.
    Liz Vanderlinde
    Infection Prevention Control Co-ordinator
    North West Private Hospital
    [Description: hca_luye_logo]
    Brickport Road, Burnie TAS 7320, Australia
    T +61 3 6432 6005 F +61 3 6431 5766
    E liz.vanderlinde@healthecare.com.au W healthecare.com.au
    Healthe Care Hospitals are accredited by ACHS NSQHS Standards or ACHS EQuIP National
    [Description: achs][Description: equip]
    QIC Standards
    [Description: qic]
    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to acipclist@acipc.org.au

    To send a message to the list administrator send an email to admin@acipc.org.au

    You can unsubscribe manually from this list by sending ‘signoff acipclist’ (without the quotes) to listserv@aicalist.org.au

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to acipclist@acipc.org.au

    To send a message to the list administrator send an email to admin@acipc.org.au

    You can unsubscribe manually from this list by sending ‘signoff acipclist’ (without the quotes) to listserv@aicalist.org.au

    #77308
    Anonymous
    Inactive

    Author:
    Anonymous

    Organisation:

    State:

    Dear Liz,

    When I installed our new sterilizes there was a requirement detailed on the installation specifications that we have to install an extraction vent over the sterilizer, it doesn’t reference any standards though.

    Cheers,

    Sharee Williams
    Director of Nursing
    Hervey Bay Surgical Hospital
    phone: 07 4194 4000
    fax: 07 41282191
    email: Shareew@hbsurgical.com

    Good Morning One and All

    During a recent audit we had a recommendation regarding the placement of outlet vents in the ceiling above the Steriliser doors.
    Temperatures in our CSSD Department become quite warm so looking for a reference that supports this
    Can anyone assist please

    Most appreciated.
    Liz Vanderlinde
    Infection Prevention Control Co-ordinator
    North West Private Hospital
    [Description: hca_luye_logo]
    Brickport Road, Burnie TAS 7320, Australia
    T +61 3 6432 6005 F +61 3 6431 5766
    E liz.vanderlinde@healthecare.com.au W healthecare.com.au
    Healthe Care Hospitals are accredited by ACHS NSQHS Standards or ACHS EQuIP National
    [Description: achs][Description: equip]
    QIC Standards
    [Description: qic]
    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to acipclist@acipc.org.au

    To send a message to the list administrator send an email to admin@acipc.org.au

    You can unsubscribe manually from this list by sending ‘signoff acipclist’ (without the quotes) to listserv@aicalist.org.au

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to acipclist@acipc.org.au

    To send a message to the list administrator send an email to admin@acipc.org.au

    You can unsubscribe manually from this list by sending ‘signoff acipclist’ (without the quotes) to listserv@aicalist.org.au

    #77310
    Andrew Ellis
    Participant

    Author:
    Andrew Ellis

    Email:
    andrew.ellis@sa.gov.au

    Organisation:
    SA Health

    State:
    SA

    Hi Liz,

    The Australasian Health Facility guidelines specify in HPU B.0190 Sterilizing Services Unit under the section on loading and unloading areas of sterilisers that:

    “A duct enclosure can also minimise heat build-up within the Workroom. An exhaust over the front of the sterilizer/s should also be considered, to extract both heat (cabinet) and steam (opening door)”. The AusHFG are the standard for facility design and this would be the likely reason.

    AS/NZS4187:2014 5.6.1 also states “[The physical environment] shall include requirements for environmental control in areas that can impact the bioburden of an RMD, e.g. control of temperature, humidity, traffic flow, and reprocessing, ventilation and air flow”. If the sterilisers open onto a storage area then excess heat may impact on clause A9.5 (f) “The temperature within the storage area should be controlled within the range of 18C to 25C”.

    Regards,

    Andrew Ellis
    Sterilising and Reusable Medical Device Reprocessing State Coordinator
    Infection Control Service | Communicable Disease Control Branch
    Health Regulation & Protection
    Department for Health and Wellbeing | Government of South Australia
    Level 13 | 25 Grenfell Street | Adelaide SA 5000
    HCW infection prevention: http://www.sahealth.sa.gov.au/infectionprevention
    General public: http://www.sahealth.sa.gov.au/hospitalinfections

    This email may contain confidential information, which also may be legally privileged. Only the intended recipient(s) may access, use, distribute or copy this email. If this email is received in error, please inform the sender by return email and delete the original. If there are doubts about the validity of this message, please contact the sender by telephone. It is the recipient’s responsibility to check the email and any attached files for viruses.

    Good Morning One and All

    During a recent audit we had a recommendation regarding the placement of outlet vents in the ceiling above the Steriliser doors.
    Temperatures in our CSSD Department become quite warm so looking for a reference that supports this
    Can anyone assist please

    Most appreciated.
    Liz Vanderlinde
    Infection Prevention Control Co-ordinator
    North West Private Hospital
    [Description: hca_luye_logo]
    Brickport Road, Burnie TAS 7320, Australia
    T +61 3 6432 6005 F +61 3 6431 5766
    E liz.vanderlinde@healthecare.com.au W healthecare.com.au
    Healthe Care Hospitals are accredited by ACHS NSQHS Standards or ACHS EQuIP National
    [Description: achs][Description: equip]
    QIC Standards
    [Description: qic]
    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to acipclist@acipc.org.au

    To send a message to the list administrator send an email to admin@acipc.org.au

    You can unsubscribe manually from this list by sending ‘signoff acipclist’ (without the quotes) to listserv@aicalist.org.au

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to acipclist@acipc.org.au

    To send a message to the list administrator send an email to admin@acipc.org.au

    You can unsubscribe manually from this list by sending ‘signoff acipclist’ (without the quotes) to listserv@aicalist.org.au

    #77311
    Lalith Ramachandra
    Participant

    Author:
    Lalith Ramachandra

    Email:
    lalith.ramachandra@GMAIL.COM

    Organisation:

    State:

    Hello Liz

    Most sterilisers are built-in i.e. located between two ss walls.

    This cavity is generally vented (exhausted) to remove heat buildup and
    moisture (to avoid condensation).

    The loading/packing area is generally segregated and is at a lower pressure
    than the unloading and the sterile stock room. It’s unclear from the email
    which side is getting warm.

    A single supply air vent above the door is unlikely to do much if the whole
    area is getting warm. It’s most likely that the a/c unit is
    undersized and/or there is inadequate supply air into the room or there is
    no exhaust within the cavity.

    Hope this helps.

    Cheers

    Lalith Ramachandra
    LR Consulting Engineers

    PO Box 40968
    Casuarina, NT
    p 0401117423
    e lalith.ramachandra@gmail.com

    * To Spot the Expert, Pick the One Who Predicts the Job Will Take the
    Longest and Cost the Most!*

    On Tue, 15 Sep 2020 at 10:30, VANDERLINDE, Liz wrote:

    > Good Morning One and All
    >
    >
    >
    > During a recent audit we had a recommendation regarding the placement of
    > outlet vents in the ceiling above the Steriliser doors.
    >
    > Temperatures in our CSSD Department become quite warm so looking for a
    > reference that supports this
    >
    > Can anyone assist please
    >
    >
    >
    > Most appreciated.
    >
    > *Liz Vanderlinde*
    > Infection Prevention Control Co-ordinator
    > *North West Private Hospital*
    >
    > [image: Description: hca_luye_logo]
    >
    > Brickport Road, Burnie TAS 7320, Australia
    > *T* +61 3 6432 6005 *F* +61 3 6431 5766
    > *E* liz.vanderlinde@healthecare.com.au *W* healthecare.com.au
    >
    > Healthe Care Hospitals are accredited by ACHS NSQHS Standards or ACHS
    > EQuIP National
    > [image: Description: achs][image: Description: equip]
    > QIC Standards
    > [image: Description: qic]
    >
    > Disclaimer: This email, which includes information and data located in any
    > attachments, links, portals or associated interface, is private and
    > confidential and is intended only for the use of the addressee(s) named
    > above. This email may contain information that is privileged, commercial in
    > confidence, private or subject to copyright and other intellectual property
    > rights. If you are not the intended recipient of this message you are
    > hereby notified that you must not disseminate, copy or take any action or
    > assist any third party to take any action based on its contents. Any
    > “personal Information” or “sensitive information” contained in this email
    > is subject to the Privacy Act 1988 (Cth) and any prohibited use of such
    > information may result in severe penalties being imposed. If you received
    > this message in error please notify Healthe Care Australia immediately and
    > delete and destroy the email from your computer.
    > MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO
    > NOT REPRESENT THE OPINION OF ACIPC.
    >
    > The use of trade/product/commercial brand names through the list is
    > discouraged by ACIPC. If you wish to discuss specific reference to products
    > or services by brand or commercial names, please do this outside the list.
    >
    > Archive of all messages are available at http://aicalist.org.au/archives
    > – registration and login required.
    >
    > Replies to this message will be directed back to the list. To create a new
    > message send an email to acipclist@acipc.org.au
    >
    > To send a message to the list administrator send an email to
    > admin@acipc.org.au
    >
    > You can unsubscribe manually from this list by sending ‘signoff acipclist’
    > (without the quotes) to listserv@aicalist.org.au
    >

    MESSAGES POSTED TO THIS LIST ARE SOLELY THE OPINION OF THE AUTHOR, AND DO NOT REPRESENT THE OPINION OF ACIPC.

    The use of trade/product/commercial brand names through the list is discouraged by ACIPC. If you wish to discuss specific reference to products or services by brand or commercial names, please do this outside the list.

    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

    Replies to this message will be directed back to the list. To create a new message send an email to acipclist@acipc.org.au

    To send a message to the list administrator send an email to admin@acipc.org.au

    You can unsubscribe manually from this list by sending ‘signoff acipclist’ (without the quotes) to listserv@aicalist.org.au

Viewing 5 posts - 1 through 5 (of 5 total)
  • The forum ‘Infexion Connexion’ is closed to new topics and replies.