Combined Negative/Postive isolation room

Home Forums Infexion Connexion Combined Negative/Postive isolation room

 | Click to Receive Email Notifications of Posts
Viewing 3 posts - 1 through 3 (of 3 total)
  • Author
    Posts
  • #68318
    Wishart, Michael
    Participant

    Author:
    Wishart, Michael

    Position:

    Organisation:

    State:

    [Posted on behalf of Mary-Rose Godsell – Moderator]

    Dear All,
    I have been asked to investigate the possibility of including a room that
    can have both negative pressure and then be changed into a positive
    pressure isolation room – (so interchangable) for some upcoming
    renovation in an ICU and ED.
    I haven’t read in the literature or heard of this being a viable option,
    however would like to canvass the AICA list to gather some evidence
    around this. Also the efficacy of using positive pressure isolation
    rooms in the first instance.

    Thank you
    Regards
    Mary-Rose Godsell
    RGON, AFAAQHC, GDipHSM, CICP, MAdvancedPrac(Infection Control)
    South West Infection Control Nurse Consultant
    WA Country Health Service

    ‘Hand hygiene reduces the
    spread of infection’

    ph:08) 9722 1490
    mobile 04 3996 1015
    e-mail: Mary-Rose.Godsell@health.wa.gov.au

    > The contents of this email, including any attachments sent with it,
    > are confidential. The contents are intended only for the named
    > recipient of this email. If the reader of this email is not the
    > intended recipient, please note that any use, reproduction, disclosure
    > or distribution of the information contained in this email must not
    > occur with the express permission of the sender If you have received
    > this email in error, please notify the sender.
    >
    >
    >

    This e-mail message and any accompanying files may contain
    information that is confidential and subject to privilege. If you
    are not the intended recipient, and have received the e-mail
    in error, you are notified that any use, dissemination,
    distribution, forwarding, printing or copying of the message
    and any attached files is strictly prohibited. If you have
    received this e-mail message in error please immediately
    advise the sender by return e-mail, or telephone 1800 243 903.
    You must destroy the original transmission and its contents.
    Any views expressed within this communication are those of
    the individual sender, except where the sender specifically
    states them to be the views of Ramsay Health Care.
    This communication should not be copied or disseminated
    without permission.
    ————————————————————————

    Messages posted to this list are solely the opinion of the authors, and do not represent the opinion of AICA.
    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.
    Replies to this message will be directed back to the list. To create a new message send an email to aicalist@aicalist.org.au
    To send a message to the list administrator send an email to aicalist-request@aicalist.org.au.
    You can unsubscribe from this list be sending ‘signoff aicalist’ (without the quotes) to listserv@aicalist.org.au

    #68322
    Wishart, Michael
    Participant

    Author:
    Wishart, Michael

    Position:

    Organisation:

    State:

    [Posted on behalf of John Ferguson – Moderator]

    Dear Mary-Rose

    At HIS meeting 3 or 4 yrs ago I heard described such a room design
    together with a detailed experimental evaluation conducted to prove it
    worked. It involved a positive pressure anteroom (with filtered air
    going in) and air egress via the ensuite that was entered from within
    the room. For a while they had a building design note available. But
    this has gone and I’ve made another search without success (might be
    worth a pubmed look)

    This may help- some discussion of CDC requirements and the design
    elements of isolation rooms-

    http://books.google.com.au/books?idq_Q_ncugJX4C&pgPA1003&lpgPA1003&dq
    %22positive+pressure+anteroom%22+isolation&sourcebl&otsCmEJM6Q1DP&sig
    qQzUZQmjW6nQQnynLPsNmQvrjJg&hlen&ei3G8lTIumPNCGcYHXzKYC&saX&oibook_
    result&ctresult&resnum1&ved0CAYQ6AEwAA#vonepage&q%22positive%20pres
    sure%20anteroom%22%20isolation&ffalse

    I will make enquiries to the Univ group that manages the Australasian
    facility guidelines

    best wishes

    John

    Reply from Aus Fac Guideline head at UNSW Jane Carthey below to append
    to my reply

    John, good to hear from you. The official line here in Oz is not to go
    with the changeable pressure rooms as they are considered unreliable.
    However I have just got back from Europe and have seen examples there
    that seemed to work just fine – I think it was in the Netherlands. You
    may be able to get further information from Joram Nauta at Dutch TNO
    (Dutch Centre for Health Assets and Architecture) who organised our tour
    and the conference I attended – very helpful chap!

    Dr John Ferguson
    Director, Infection Prevention and Control Unit
    Microbiologist and Infectious Diseases Physician
    Hunter New England Health Service
    Locked Bag 1, Newcastle, NSW 2310, Australia
    tel 61 2 49214422, fax 61 2 49214440

    Go to http://www.hicsiganz.org for ANZ healthcare infection control resources
    and networking.

    Messages posted to this list are solely the opinion of the authors, and
    do not represent the opinion of AICA. Archive of all messages are
    available at http://aicalist.org.au/archives – registration and login
    required. Replies to this message will be directed back to the list. To
    create a new message send an email to aicalist@aicalist.org.au To send a
    message to the list administrator send an email to
    aicalist-request@aicalist.org.au. You can unsubscribe from this list be
    sending ‘signoff aicalist’ (without the quotes) to
    listserv@aicalist.org.au

    This e-mail message and any accompanying files may contain
    information that is confidential and subject to privilege. If you
    are not the intended recipient, and have received the e-mail
    in error, you are notified that any use, dissemination,
    distribution, forwarding, printing or copying of the message
    and any attached files is strictly prohibited. If you have
    received this e-mail message in error please immediately
    advise the sender by return e-mail, or telephone 1800 243 903.
    You must destroy the original transmission and its contents.
    Any views expressed within this communication are those of
    the individual sender, except where the sender specifically
    states them to be the views of Ramsay Health Care.
    This communication should not be copied or disseminated
    without permission.
    ————————————————————————

    Messages posted to this list are solely the opinion of the authors, and do not represent the opinion of AICA.
    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.
    Replies to this message will be directed back to the list. To create a new message send an email to aicalist@aicalist.org.au
    To send a message to the list administrator send an email to aicalist-request@aicalist.org.au.
    You can unsubscribe from this list be sending ‘signoff aicalist’ (without the quotes) to listserv@aicalist.org.au

    #68329
    TERRI CRIPPS
    Participant

    Author:
    TERRI CRIPPS

    Position:

    Organisation:

    State:

    Hi Mary-Rose,

    My facility has rooms where you can switch them over from positive to negative pressure which were built 10-15 years ago. I find that on occasion that staff will switch the room to negative pressure when there really was no need to do so (eg with Norovirus!) and this usually occurs over a weekend! We also have 4 dedicated rooms which have positive pressure which are used for our bone marrow transplant patients but I am not sure exactly how effective they are as there is a shared bathroom between each pair.

    The previous facility I worked in had negative pressure rooms that were dedicated as such and only the engineering people could turn them off. There was a few rooms in ICU that were able to be switched over but no one was ever taught how to do it and the switches were hidden so only engineering did those ones too (luck really).

    The literature that Lindy Ryan suggested is the ones that I have read also and is helpful.

    Good luck with the renovations.

    Terri Cripps | CNC Infection Control | Sydney Children’s Hospital
    ‘: (02) 9382 1876 | fax: (02) 9382 2084 |* : terri.cripps@sesiahs.health.nsw.gov.au| “:www.sch.edu.au| page: 47140

    ________________________________

    [Posted on behalf of Mary-Rose Godsell – Moderator]

    Dear All,
    I have been asked to investigate the possibility of including a room that
    can have both negative pressure and then be changed into a positive
    pressure isolation room – (so interchangable) for some upcoming
    renovation in an ICU and ED.
    I haven’t read in the literature or heard of this being a viable option,
    however would like to canvass the AICA list to gather some evidence
    around this. Also the efficacy of using positive pressure isolation
    rooms in the first instance.

    Thank you
    Regards
    Mary-Rose Godsell
    RGON, AFAAQHC, GDipHSM, CICP, MAdvancedPrac(Infection Control)
    South West Infection Control Nurse Consultant
    WA Country Health Service

    ‘Hand hygiene reduces the
    spread of infection’

    ph:08) 9722 1490
    mobile 04 3996 1015
    e-mail: Mary-Rose.Godsell@health.wa.gov.au

    > The contents of this email, including any attachments sent with it,
    > are confidential. The contents are intended only for the named
    > recipient of this email. If the reader of this email is not the
    > intended recipient, please note that any use, reproduction, disclosure
    > or distribution of the information contained in this email must not
    > occur with the express permission of the sender If you have received
    > this email in error, please notify the sender.
    >
    >
    >

    This e-mail message and any accompanying files may contain

    information that is confidential and subject to privilege. If you

    are not the intended recipient, and have received the e-mail

    in error, you are notified that any use, dissemination,

    distribution, forwarding, printing or copying of the message

    and any attached files is strictly prohibited. If you have

    received this e-mail message in error please immediately

    advise the sender by return e-mail, or telephone 1800 243 903.

    You must destroy the original transmission and its contents.

    Any views expressed within this communication are those of

    the individual sender, except where the sender specifically

    states them to be the views of Ramsay Health Care.

    This communication should not be copied or disseminated

    without permission.

    ————————————————————————

    Messages posted to this list are solely the opinion of the authors, and do not represent the opinion of AICA. Archive of all messages are available at http://aicalist.org.au/archives – registration and login required. Replies to this message will be directed back to the list. To create a new message send an email to aicalist@aicalist.org.au To send a message to the list administrator send an email to aicalist-request@aicalist.org.au. You can unsubscribe from this list be sending ‘signoff aicalist’ (without the quotes) to listserv@aicalist.org.au

    ———————————————————————————————

    SOUTH EASTERN SYDNEY AND ILLAWARRA AREA HEALTH SERVICE CONFIDENTIALITY NOTICE

    This email, and the files transmitted with it, are confidential and intended solely for the use of the individual or entity to whom they are addressed. If you are not the intended recipient, you are not permitted to distribute or use this email or any of its attachments in any way. We also request that you advise the sender of the incorrect addressing.

    This email message has been virus-scanned. Although no computer viruses were detected, South Eastern Sydney and Illawarra Area Health Service accept no liability for any consequential damage resulting from email containing any computer viruses.

    Messages posted to this list are solely the opinion of the authors, and do not represent the opinion of AICA.
    Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.
    Replies to this message will be directed back to the list. To create a new message send an email to aicalist@aicalist.org.au
    To send a message to the list administrator send an email to aicalist-request@aicalist.org.au.
    You can unsubscribe from this list be sending ‘signoff aicalist’ (without the quotes) to listserv@aicalist.org.au

Viewing 3 posts - 1 through 3 (of 3 total)
  • The forum ‘Infexion Connexion’ is closed to new topics and replies.