Hi Sony and Michael,

The only Australian reference to linen and waste chutes is the “2003
Handbook – Hospital acquired infections – Engineering down the risks” which
states the following:

. 3.2(a) Disposal rooms para 2 – “Chutes require particular design
features and will raise ongoing maintenance and cleaning issues. In
addition, chutes can propel airborne contaminants throughout the facility.
Therefore, chutes should not be incorporated in design features for the
management of transport of waste or linen in healthcare facilities”

These standards may be somewhat out of date (i.e. 2003) as new generation
waste and linen chute systems have been introduced into Europe, Asia and the
US for use in residential, industrial, commercial and hospital and nursing
home settings.

In the US the “2010 edition of the FGI “Guidelines for Design and
Construction of Health Care Facilities”, refuse and linen chutes are
permitted and the guideline and states the following:

Refuse chutes

2.1.4 Patient Support Services

2.1-5 General Support Services and Facilities

2.1 – 5.4 Waste Management Facilities

2.1 0 5.4.1.4 Refuse chutes, If provided, these shall meet or exceed the
following standards:

(1) Chutes shall meet the provisions described in NFPA 82

(2) Service openings to chutes shall comply with NFPA 101

(3) Chute discharge into collection rooms shall comply with NFPA 101

(4) The minimum cross-sectional dimension of gravity chutes shall be 2 feet
(60.96 centimetres)

Linen chutes

2.2-5.2.6 – if provided shall meet or exceed the following standards:

2.5 -5.2.6.1 Standards

(1) Service openings to chutes shall comply with NFPA 101

(2) Chutes shall meet the provision described in NFPA 82

(3) Chute discharge into collection rooms shall comply with NFPA 101

2.2-5.2.6.2 Dimensions. The minimum cross-sectional dimensions of gravity
chutes shall be 2 feet

(60.96 centimetres)

The NFPA is the US “National Fire Protection Association”

In addition the USA DRAFT – 2014 edition of the FGI “Guidelines for Design
and Construction of Health Care Facilities” includes guidelines for such
chutes.

The draft 2014 manuscript is available for public comment can be accessed at
the following link: http://www.fgiguidelines.net/comments/draft.php

Regards

Glenys

Glenys Harrington

Consultant

Infection Control Consultancy (ICC)

PO Box 5202

Middle Park

Victoria, 3206

Australia

H: +61 3 96902216

M: +61 404 816 434

infexion@ozemail.com.au

ABN 47533508426

Of Michael Wishart
&/or waste chute

Hi Sony

My understanding is that in Australia, most new hospital buildings, and
indeed those being refurbished, have removed linen and waste chutes due to
fire regulations prohibiting them. So I would not think there are many
hospitals with these kinds of chutes left in this country.

Cheers
Michael Wishart

Michael Wishart

CNC Infection Control

Holy Spirit Northside Private Hospital

627 Rode Road, Chermside, Qld 4032

t: (07) 3326 3068 | f: (07) 3326 3523

e: Michael.Wishart@hsn.org.au

w:
http://www.holyspiritnorthside.org.au

Please consider the environment before printing this email

_____

SO [sony@HA.ORG.HK]

Dear All,

We are preparing our hospital renovation project, hence we would like to
know whether you would use linen chute &/or waste chute.

Your sharing would be a tremendous help.

Regards,

Sony SO

Nursing Officer, Infection Control Team

Kwong Wah Hospital

HONG KONG SAR, CHINA

Tel:+ 852 3517-2409 Fax: +852 2332-3348 email:sony@ha.org.hk

Please consider the environment before printing this e-mail

_____

***************************************************************************
Disclaimer

This Email may contain privileged and confidential information and is solely
for the use of the intended recipient. If you are not the intended
recipient, you must not print, copy, distribute or take any action in
reliance on it. If you have received this Email by mistake, please notify
the sender and then delete this Email from your computer. The Hospital
Authority does not accept liability arising from Email transmitted by
mistake.

Although this Email and any attachments are believed to be free of virus or
other defects that might affect any computer system into which it is
received and opened, it is the responsibility of the recipient to ensure
that it is virus free, and no responsibility is accepted by the Hospital
Authority for any loss or damage in any way arising from its use.

All views or opinions expressed in this Email and its attachments are those
of the sender and do not necessarily reflect the views and opinions of the
Hospital Authority.
***************************************************************************
Messages posted to this list are solely the opinion of the authors, and do
not represent the opinion of ACIPC.

Archive of all messages are available at http://aicalist.org.au/archives
registration and login required.

Replies to this message will be directed back to the list. To create a new
message send an email to aicalist@aicalist.org.au

To send a message to the list administrator send an email to
aicalist-request@aicalist.org.au.

You can unsubscribe from this list be sending ‘signoff aicalist’ (without
the quotes) to listserv@aicalist.org.au

Message protected by MailGuard: e-mail anti-virus, anti-spam and content
filtering.
http://www.mailguard.com.au/mg

Report this message as spam

WARNING : This email contains information, which is CONFIDENTIAL, and that
maybe subject to LEGAL PRIVILEGE. This e-mail and any attachments to it (the
“Communication”) is confidential and is for the use only of the intended
recipient, and may not duplicated or used by any other party without the
express consent of the sender. The Communication may contain copyright
material of St Vincent’s Health & Aged Care(“SVHAC”), or any of its related
entities or of third parties. If you are not the intended recipient of the
Communication, please notify the sender immediately by return e-mail, delete
the Communication, and do not read, copy, print, retransmit, store or act in
reliance on the Communication. Any views expressed in the Communication are
those of the individual sender only, unless expressly stated to be those of
SVHAC. SVHAC does not guarantee the integrity of the Communication, or that
it is free from errors, viruses or interference. Thank-you.

Message protected by MailGuard: e-mail anti-virus, anti-spam and content
filtering.
http://www.mailguard.com.au/mg

Messages posted to this list are solely the opinion of the authors, and do
not represent the opinion of ACIPC.

Archive of all messages are available at http://aicalist.org.au/archives
registration and login required.

Replies to this message will be directed back to the list. To create a new
message send an email to aicalist@aicalist.org.au

To send a message to the list administrator send an email to
aicalist-request@aicalist.org.au.

You can unsubscribe from this list be sending ‘signoff aicalist’ (without
the quotes) to listserv@aicalist.org.au

Messages posted to this list are solely the opinion of the authors, and do not represent the opinion of ACIPC.

Archive of all messages are available at http://aicalist.org.au/archives – registration and login required.

Replies to this message will be directed back to the list. To create a new message send an email to aicalist@aicalist.org.au

To send a message to the list administrator send an email to aicalist-request@aicalist.org.au.

You can unsubscribe from this list be sending ‘signoff aicalist’ (without the quotes) to listserv@aicalist.org.au